Bloody hell you would have to be very skilled with the saw to manage the same depth right the way along a run of say 5m. I'm not sure I am happy to use a stihl saw on a floor where I have no bearings on main incomer, gas or water pipes. Just don't know the best option but safety is always first though.
 
a FLOORSAW has depth gauge and you can set to depth as for incomming supplies they should be on drawing
electricity use a CAT
gas follow from meter to appliance
water you might get wey unless you can locate vissualy
 
To accurately cut a depth with a stihl saw you run the hub of the saw on a piece of timber of appropiate thickness to give the require depth, simples.
 
Even if I was to run across gurders. There would then be 5m + of swa floating from the ceiling unsupported to car ramp. Surely this would be against regs?
 
Or fit some uni strut from the griders,then bolting the foot to the floor,running it adjacent to, and fixed to the ramp post.then swa run inside the strut
 
Or fit some uni strut from the griders,then bolting the foot to the floor,running it adjacent to, and fixed to the ramp post.then swa run inside the strut

Unistrut is one of the sturdiest forms of protecting cables. You could get a 6m length of double uni, bolt it from the purlins, to the lift and bobs your uncle.
 
Unit floor to girders mounjt isolator on uni incase ramp needs replaced as most ramps iv seen have removable panels for servicing,repair
UNI if joined properly is very rigid and could create quite a span
 
If built well enough it should last, obviously concreting would be a better option. Chasing out would be better option again I agree.

Just giving the OP ideas as they know the situation better than any of us.

If it was a viable solution to build it well enough the cost of the timber would be prohibitively expensive, cheaper to chop the floor out IMO and a better solution
 
You can get a car in but you cant get a cherry picker in? I am definitely missing something aren't I:yesnod:
 
Right if I notch out floor and put 6mm singles through 25mm steel conduit. The depth of the buried cable would not be against regs because its protected by steel conduit? Could I then just cement over conduit? Really I would like to notch out just enough so that conduit is sunk around 50mm. I do not fancy going deeper than that for obvious reasons.
 
When we do any major work on refurbs, or full new builds, we always obtain site plans showing incoming services. Not sure on prices but if you contact the local water board, gas supplier, etc, they should be able to help.

Could save you a lot of hassle if you did come a cropper on a water pipe !
 