Right if I notch out floor and put 6mm singles through 25mm steel conduit. The depth of the buried cable would not be against regs because its protected by steel conduit? Could I then just cement over conduit? Really I would like to notch out just enough so that conduit is sunk around 50mm. I do not fancy going deeper than that for obvious reasons.
You may find that what you think is concrete is in fact a cement screed cover over the concrete base floor. Screed is nowhere near as hard to chop out as concrete and is normally around 4'' depth in most cases.
What you suggest is quite acceptable, whether you use singles in metal conduit or SWA in PVC duct. Chopping the floor out for your cable run, is really your only feasible option from what you have told us here in your thread...