Hi,
I've just completed some fault finding on a ring final, as I couldn't get continuity on the CPC, and I found most of the metal back boxes and CPC conductors were in a pretty bad state with lots of corrosion. I did a bit of cleaning up to get bare copper, and it worked enough to get continuity, but the values were still quite bad. Has anyone tried the vinegar/salt and then baking soda method to clean copper to recover corroded conductors and metal back boxes ? It's only the lugs on the back boxes and the first 10mm or so on the conductors, but I don't want to cut them back as there won't be enough conductor left to fix the fronts on.
 
Why is it all corroded?

If its a load of water etc then cleaning would be OK.

However if its the green goo - this could be a bigger problem, this could extend up the core all the way. This was caused by a poor choice of plasticiser for the pvc used in the 1960's which desolved the conductors themselves.

This can cause the cross section to be significantly reduced, this isn't a case of cleaning, as the cable is completely destroyed.

Cable from the mid-late '70s should be ok as the issue was resolved.

Remember the goo is toxic and conductive, another issue therefore is at the bottom of vertical runs it spreads out and can cause short circuits.
 
I would be very weary of using any sort of corrosive mix to try and out-corrode existing damage. Most likely it will persist somewhere after you think it is finished and cause more problems for later.

Realistically if it is beyond a bit of a scrub with a small wire brush or wire-wool, then you really should be looking at replacement.
 
Couple squirts of white vinegar solution and scrub with a wire scouring pad To clean old cables. If the back box is all rusted up it could be damp wall so the damp will need sorting then replace the back box.
 
The back boxes were all dry, so I'm not suspecting a water leak. Cables were all renewed in roughly 2012 (That's the date on the consumer unit). My suspicion is that the fronts were put back on before the plaster dried (There were plaster splashes on the back of the front plates), thus it was "damp" behind the fronts. I've looked into it a bit more, and it's common for the CPC to be affected by corrosion and not the other conductors if damp, condensation etc is involved, and I believe old lime based plaster can react with the zinc in the back boxes and the copper in the conductors if any amount of water is introduced.

I've seen one solution to this is to use plastic back boxes where lime plaster is suspected to form a barrier between the plasterwork and the cables.

Anyway I'm due back on Monday, so I'll clean it all up, replace any fly leads and fronts that are beyond repair and see what readings I get for continuity and IR and take it from there.

btw there is a video up on youtube on this, so comments welcome.
 
The back boxes were all dry, so I'm not suspecting a water leak. Cables were all renewed in roughly 2012 (That's the date on the consumer unit). My suspicion is that the fronts were put back on before the plaster dried (There were plaster splashes on the back of the front plates), thus it was "damp" behind the fronts. I've looked into it a bit more, and it's common for the CPC to be affected by corrosion and not the other conductors if damp, condensation etc is involved, and I believe old lime based plaster can react with the zinc in the back boxes and the copper in the conductors if any amount of water is introduced.

I've seen one solution to this is to use plastic back boxes where lime plaster is suspected to form a barrier between the plasterwork and the cables.

Anyway I'm due back on Monday, so I'll clean it all up, replace any fly leads and fronts that are beyond repair and see what readings I get for continuity and IR and take it from there.

btw there is a video up on youtube on this, so comments welcome.
post a link to the video.
 

Reply to Cleaning corroded conductors in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
599
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
979
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock