Hey Lionel.

Code 1 = Requires urgent attention
Code 2 = Requires improvement
Code 3 = Requires further investigation
Code 4 = Does not comply with BS 7671

These codes are applied to any issues found on a periodic inspection and range from very bad i.e Code 1 - access live parts, absence of earthing conductor to Code 4 - no indicator sleeving on switch wires, no circuit schedule at DB.

Hope this helps.
 
Do the codes only apply when carrying out a periodic inspection report??,
and also what do you need to do if you come across a code 1, do you stop everything and make safe etc?..:)
Thanks
 
Hi Dan.

Well the only time you would need to assign a code to an item is when you found it on a PIR and noted it in on the relevant page. If you found a problem whilst carrying out some other work then you could class it as one of the codes and note it in the comments on existing installation box on the EIC/MW you were doing for the work you had carried out.

Ideally yes a code 1 should be rectified straight away without delay.

Hope this helps.
 
An extract from professional electrician Nov 2008

Code 1 REQUIRES URGENT ATTENTION
Indicates immediate danger
The installation is a risk to the user; therefore , the inspector should take appropriate action without delay to remove the danger

Code 2 REQUIRES IMPROVEMENT
This code should be used to indicate that the observed fault requires action to remove Potential danger

CODE 3 REQUIRES FURTHER INVESTIGATION
Indicates that the inspection has revealed an apparent deficiency which could not be fully identified and
should be investigated further

CODE 4 DOES NOT COMPLY
With the current edition of BS7671 but are not deemed a risk to the user

hth Jim
 

Reply to codes in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
526
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
372
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
623
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock