Thought about running a 6x6 galv trunking as low as possible to gland into then, fit a KMF on top of the trunk for each meter and tail out in 25mm double insulated and maybe a Henley block for the cpcs.Does this make sense?
 
To my mind each isolator should be replaced with a switch fuse unit. The SWA’s need terminating properly.
How the hell you do it in the space available I don’t know.
The isolators are DNO property so would have to stay.I assume the submains would require fuse protection on the consumer side
 
The isolators are DNO property so would have to stay.I assume the submains would require fuse protection on the consumer side


Absolutely.

How long are those sub-mains???

The DNO rule of thumb is 3M before you need to offer additional overcurrent protection as they will not guarantee reliance on their service fuse.
 