Just doing an inspection report on an installation where they have used connectors or chock block terminations on all lights. No ceiling rose's fitted. But light has fancy dome unit screwed direct to ceiling with pedant. Connectors fitted look like 15A version no tape used to give further protection. All cores correctly identified.

Question
  • should 17th edition Wago type connectors be used as installed correctly the insulation is taken inside the connector.
  • Should insulation tape be used to provide better indirect protection.
  • Is it a C3 at best
  • Or am I being too fussy. I always use Wago type connectors never use chock block type.
  • Job is couple years old

AdieB
 
As long as copper isn't spilling out of the connectors they are fine, they are accessible for inpection if required and screw terminal connectors are still aceptable anyway that is open to inspection... as for tape - the connector insulation is adequate and is housed in the fittings base cup which acts as a cover just like singles run in trunking.

A tad fussy then seen as you ask.
 
Just doing an inspection report on an installation where they have used connectors or chock block terminations on all lights. No ceiling rose's fitted. But light has fancy dome unit screwed direct to ceiling with pedant. Connectors fitted look like 15A version no tape used to give further protection. All cores correctly identified.

Question
  • should 17th edition Wago type connectors be used as installed correctly the insulation is taken inside the connector.
  • Should insulation tape be used to provide better indirect protection.
  • Is it a C3 at best
  • Or am I being too fussy. I always use Wago type connectors never use chock block type.
  • Job is couple years old

AdieB

Answers
  • 17th edition connectors ? Wagos may comply with certain regs where screw connectors won't in certain situations.... but this isn't one of them.
  • No. The insulation of the connector block is fine as long as the terminations are made correctly. The standard for protection of live parts is IP2X, which is obviously afforded by connectors.
  • No code.
  • Yes too fussy. I nearly always use push connectors myself though.
  • No problems.
 
Yes I agree to fussy. When I mentioned 17th edition connectors I was talking about the Wago type. Where the cores are taken inside the connector via individual slots as apposed to twisted together into one slot. Where as the old connector does afford some plastic insulation its not as good (in m(y opinion). My initial concern was that 15A connectors were used giving a larger gap around the termination Would not of been so obvious if say 6A connector was used.

AdieB
 
Yes I agree to fussy. When I mentioned 17th edition connectors I was talking about the Wago type. Where the cores are taken inside the connector via individual slots as apposed to twisted together into one slot. Where as the old connector does afford some plastic insulation its not as good (in m(y opinion). My initial concern was that 15A connectors were used giving a larger gap around the termination Would not of been so obvious if say 6A connector was used.

AdieB

For a condition report all codings should be referenced against a regulation, as the report is an assessment based on the regulations. I appreciate what you are saying regarding best practise, but that doesn't really come into it. The report is about minimum requirements and compliance with them. The plastic screw connector does not afford as good an ingress rating as a wago, but unless you can reference a reg that directly states this level of ingress protection is not permitted, then it shouldn't be considered for a coding.
Don't get into a habit of being too fussy with reports or they may start to become misleading.
 
Is the dome metallic? Can single-insulated wiring or choc block touch it? Is it solidly earthed?
 