the next common size would be Lenny`s 30A breaker (he should really have said 32A but he still thinks 3036s are new)
I was referring to the Ib not In.
Cant beat a good old 3036 mind.

the next common size would be Lenny`s 30A breaker (he should really have said 32A but he still thinks 3036s are new)




Applying diversity to a cooker is as follows.
Take the full load, 39.13A.
Take the first 10A of this, add 30% of the remaining current i.e 30% x 29.13 = 8.73A
Total load after diversity = 10A + 8.73A = 18.73A.
Also if the control unit has a socket outlet incorporated then you add an additional 5A.

I know it does, but was trying to be sarchastic. Just pointing the OP back to the same question he asked a bit ago

Are you guys being serious??