Popped back today to look into this one further. Cable to the oven is 10mm not the 6mm I previously quoted, so apologies to all I should have looked closer! and thanks for replying.
So I will add a socket at the connection point behind the oven.

The problem now is with the bathroom, the customer wants to move the existing shaver socket and replace it with a shaver socket and light unit. On top of that he want a new shower light and a seperate pull cord switch to turn the fan on and off and a new shower 7.2KW. All this off an exisitng 1984 Ceramic Crabtree MCB board with no RCD.
What I can not decide as to what to do is put an 80A 30ma rcd before the whole board or pull the lighting circuit and shower circuit off the board and run it through a seperate RCD.
Can I get a 80A 30ma RCD main Breaker big enough for tails? I am struggling to find one.
The best option seems to be an RCD in front of the main board, there are already three sets of tails in a tight space for storage heating.
Any help would be welcome.
 
Hello Jason, can you explain that a little further please, is that because the RCD is on the wrong side of the Isolator? or am I just not understanding.
 
As Jason rightly says you cant have one RCD protecting the entire installation as there are regs now on a fault on one circuit affecting others. With one RCD a minor fault would shut down the whole lot.
Explain to the customer that a new 17th edition DB with at least 2 RCD's will be the best option for the new work to comply.Split the circuits to minimise disruption should one rcd trip...ie upstairs lights on one rcd....downstairs on the other etc. Alternatively put each circuit on an RCBO.
 
Last edited by a moderator:
As Jason rightly says you cant have one RCD protecting the entire installation as there are regs now on a fault on one circuit affecting others. With one RCD a minor fault would shut down the whole lot.
Explain to the customer that a new 17th edition DB with at least 2 RCD's will be the best option for the new work to comply.Split the circuits to minimise disruption should one rcd trip...ie upstairs lights on one rcd....downstairs on the other etc. Alternatively put each circuit on an RCBO.
What about customers who wont pay for 17th edition CU.Main RCD switch is the only option:eek:
 
As it happens I spoke with the customer today and he reluctantly agreed to a new board, but that in itself is a new challenge, the exisitng board is in a metal enclosure surrounded by storage heating controls. I will take a picture on friday, will be interested in your comments.
My main interest in the RCD before the CU is that of an earlier post. I have been asked to do some work elsewhere, outside lights, socket, down lights and when I turn up to have a look there is this 80A 30ma RCD in front of a wylex 100A main switch MCB CU. installed last month. Straight away I am thinking that can`t be right but can not find anywhere in the regs that tells me otherwise. So then I start think could I? Though I have to say it does not sit well. Thats why I told my other customer new board or nothing this morning. Can anyone point me to the page in the red book please?
 