Cooker Isolation?

Cooker control unit switch, BS4177. Isolation (on load) = yes, Emergency switching = yes, functional switching = yes.

That is interesting Simon how does that comply with latching off if it is not under the control of a single person.

I have to be honest I'm not totally upto date with the BS 4177. So that would be interesting
 
That is interesting Simon how does that comply with latching off if it is not under the control of a single person.

I have to be honest I'm not totally upto date with the BS 4177. So that would be interesting


I am just using the information in table 53.4, it does refer to 537.4.2.5

I suppose you are referring to 537.4.2.6
 
You don't even have to use a cooker isolator if you wish. The MCB can be classed as the isolation point
 
Another foul up by the IET......ALL fixed loads should have DP isolation as a mandatory requirement IMHO
 
For what reason?

So that when the mandatory RCD's start tripping, along with unplugging all the accessories, you can also isolate fixed loads easily - then do decent IR tests with the knowledge you won't be damaging anything!
 
I'm fitting my own kitchen at the moment and I'll be installing one. Don't get me wrong, they look damned awful but 9/10 they can be easily hidden in an adjacent cupboard or unit as I will be doing and detailing the isolation point on the MEWC or EIC.


There are too many arguments in favour of installing isolation and it's good practice regardless of what the IET recommends. Considering the low cost of supply and installation, it can only be concluded as lazy by looking for loopholes in BS7671 for reasons not to install a simple switch!
 
it can only be concluded as lazy by looking for loopholes in BS7671 for reasons not to install a simple switch!

To be fair, whilst few would consider it good practice or a sensible way of doing it, it is hardly looking for loopholes in BS 7671. It quite simply isn't a requirement of the Wiring Regulations.

The double pole switch in the distribution board will suffice for any isolation requirements in a domestic premises.
 
It's a healthy debate, perhaps me saying looking for loopholes wasn't called for.

Unfortunately, my consumer unit is in a cellar accessed by a hinged door within a cupboard used for storage, which could be argued as accessible. However, my isolation point will be in the cupboard next to the cooker.

As per usual, I guess a little common sense will prevail as each job will have it's own circumstances.
 