wallyanker
I would....
32a RCBO, or MCB if CU has rcd protection already
6mm2 T&E to DP Isolator (red cooker switch)
From DP isolator, 6mm2 to double socket in adjacent cupboard to oven
Flex from oven to 13a plug and plug in socket
Flex from gas hob ignitor to plug top and plug in
This way, you can upgrade in future for a double oven that requires a 32a supply with minimal wiring alterations.