Diversitys all good till said person has a party on new years eve and...............................TRIP
 
Ah, ok.
I thought he meant apply diversity to the cooker design current and choose a MCB and cable size from that!
Yes, that is part of the system isn't it? Diversity should be applied for both individual circuits and the overall supply. Otherwise we'd have a lot of 3x6+1x16+2x32+2x50 ie around 200A (three phase needed) systems around ;)
 
Yes, that is part of the system isn't it? Diversity should be applied for both individual circuits and the overall supply. Otherwise we'd have a lot of 3x6+1x16+2x32+2x50 ie around 200A (three phase needed) systems around ;)

I meant apply diversity to the Ib then apply diversity to spec the In and CCC.
Example: Cooker with Ib of 60A apply 75% diversity would make the In and CCC 45A.
 