Hi guys new to the forum a client is wanted there new single oven installed only thing is the old one was wired in 6 mm from 32a breaker the new one is only drawing max 2000w and I suggested running new supply but this is a no because off mess it would create so trying to weigh up my options would It be feasible to change the cooker connection plate for a 13 a spur ? Any help would be appreciated
 
Of course!
The existing suppply is plenty big enough.

Leave existing circuit with 32A mcb and install FCU with 13amp fuse.
 
Ideal was thinking that install a fcu with 2.5 mm flex to cooker from 13 a fused spur cheers for the help was doing overtime thinking what would be best
 
If only all jobs were this easy...............its usually the other way round. All you need to remember is that the protective device is there to protect the circuit wiring, and there is no problem fusing down from a large cable to a small. It is probably to your advantage that you have the current set up, because i can bet the next time the kitchen is re jigged, a bigger oven will go in.

Cheers................Howard
 