E

evo6st

I have just completed a job fitting CT coils to some switch gear. All is working correctly after a bit of moving around of the CT coils to work.
The switch gear has a central T bar bus-bar running down the middle, From the cross part of the T bar (top bit) i had 3 seperate connections from the ups. The stem as it were (| bit) is terminated into the main switch. My question is how come the CT coils did not read any current flow when connected to the far left or right of the cross section which is connected to the mounting insulators but did read on the stem section between the cross section and the swwitch.
Am i right in thinking that its because there is no flow at the ends of the bus-bar were it is held in place by the insulators onto the frame of the switch gear.
 
You only get current flow between the point of supply connection on the busbar and the main switch.

Can you post a picture of the CT installation? There's a few do's and don'ts with CT's, were you supervised on the job by someone more senior? Are the CT's already connected to the metering/control device?
 
I have just completed a job fitting CT coils to some switch gear. All is working correctly after a bit of moving around of the CT coils to work.
The switch gear has a central T bar bus-bar running down the middle, From the cross part of the T bar (top bit) i had 3 seperate connections from the ups. The stem as it were (| bit) is terminated into the main switch. My question is how come the CT coils did not read any current flow when connected to the far left or right of the cross section which is connected to the mounting insulators but did read on the stem section between the cross section and the swwitch.
Am i right in thinking that its because there is no flow at the ends of the bus-bar were it is held in place by the insulators onto the frame of the switch gear.

We had some CT's installed on new switchgear today at our DC, I wanted to be there for it but am off shift at the moment and have some personal stuff to sort out, hope it wasn't my CT's you installed if your asking questions here AFTER you installed them... :D
 
The biggest worry I would have with CT's is if they were left with open circuit secondaries. I've seen large distribution boards destroyed by incorrectly installed CT's.
 
Thought so tryed to explain that to senior membesr of staff (boss) but was told not to be stupid as the whole bus-bar would have current flowing through it.
 
As above you will want to measure the full current flow of the building i assume or whatever this busbar feeds then the best place to fit CT's is over the supply tails to the busbar in fitting the CT's over the busbar's you may be monitoring part loads or as you have found no load... ie the end of the busbar.

If the senior members of staff are sparkies and told you current flow for the system is the same at any point along the busbar then they are a set of numpties and scares me too that they may be training or guiding you.

Go in tomorrow and show them this thread..... and tell them to get back to college and learn the basics.
 
Sounds like they are working without schematic switchboard drawings too, which is very worrying!! Even more so if they are building this switchboard add hock as they go along!! I don't think i've ever been on a project where switchboards, main distribution boards, of any size weren't spec'd to be factory fitted with metering and/or protection CT's
 
Yep, sounds hit and miss to me as well, I'd like to see a few photos of the finished retrofit.
 