I have my elecsa assessment next monday for which i decided to do a consumer unit change ,with bonding upgrade. unfortunately things havent gone well, first there was a neutral earth fault on the ring main which after a few hours of head scratching i traced to a joint under the lounge floor. secondly the top of the stairs light was wired on the downstairs lights but had stolen a neutral from upstairs lights hence more head scratching! also there was no earth loop at the top of stairs . anyway having sorted all the major problems out i noticed that the shower is 8.5 kw and only wired in 6mm twin and earth . should this be rectified or would the assessor be happy with it being a departure from 7671??? ps a week to go before assessment and absolutely bricking it!!!!
 
The shower would have been running on a 30A fuse anyway, therefore pop it on a 32A Type B and bobs your uncle

Cable on correct size breaker.

Can get away with a 40 under certain conditions, however leave it on a 32 and see what happens.
 
Last edited by a moderator:
sounds like standard problems you find on most CU changes, thats the whole point on testing every job first. If they were all easy we could charge £150 and all earn money. obviously you will have to rectify the issues you mention or the board change will not be compliant. Explain why you think the shower should be rectified, may be better for you to include your calculations to come to this conclusion. Believe me, this is helping you for monday.
 
A Shower at 8.5Kw will only draw 37A

A 6mm cable can take upto:
34A (if enclosed in conduit in a wall)
38A (if enclosed in conduit on top of plaster)
47A (if clipped onto the wall/in the wall with air circulating it)
51A (on a cable tray)

Have a look at the circumstance that your cable is in.

Also if it is an existing insulation that you did not put in then it is fine, you can not be held responsible for work you not completed.

Just get the MCB right - do the maths
 
Borrowed neutral on 2way landing lights are very common on cu changes, i run a sheathed single neutral and earth to the light to avoid tripping of the rcd, dont like putting both lighting on one mcb but others do.6mm cable is rated at 47amps method C so unless its run in trunking or through insulation 32 or 40amp mcb (although id go for 40) will be fine( had exactly the same on my assesment).The assessor wont even check whay rating shower is.
cheers
neil
 
cheers neil, i have done the same with the sheathed neutral earth to top of stairs so that i could split the lighting circuits on seperate rcds. the shower is clipped direct through old airing cupboard and then just a couple of metres of insulation in loft not a long run either only 10mtrs.
thanks for the help , will do more investigating before taking on another cu change, what a day!!
 
You'll be fine with your assesment , i just love faults makes the job more intresting as for the shower on a 6mm it all depends on the installation methods uses 6mm can go as low as 23.5 amps method 103 surrounded by insulation , a handy little book to have is the electricians guide to the building regs and table 2.3.1 gives you the installation methods and current carrying capacity for the cables
 
thanks ,have the book on order should be with me in the next couple of days will check it out.
 