Or even the fact that a charger does not exist at present in the premises would allow if I required by me or client the reason not to change them out. And if charger is installed by someone else then the changing of devices becomes a issue for them to change.

Yes but the circuits that provide sockets etc if there are lots of DC type loads (chargers/laptops etc) it may be prudent, but I wouldn't go with a blanket change no.
 
Some however use separate magnetic cores and the cancelling out is done on the secondary side via the wiring - this was especially the case for big MCCBs etc.

OK yes the configuration with separate CT's and balance transformer is a problem with circuit currents containing DC and could be blinded here. I've not seen that type of device in a domestic CU so would tend to discount it for the purposes of the OP's situation, but I'm not saying they don't exist.
 
OK yes the configuration with separate CT's and balance transformer is a problem with circuit currents containing DC and could be blinded here. I've not seen that type of device in a domestic CU so would tend to discount it for the purposes of the OP's situation, but I'm not saying they don't exist.
I agree I realistically picked a poor example, in hindsight I should of stuck to an industrial case - and they haven't been car chargers but other industrial equipment.


Translated it to domestic without really thinking!
 