looking at paperwork for rewire at sisters house i have done and was thinking about bathroom lights, they didn't want me to replace these although no diffuser and needing ipx4 as in zone 2. they didn't know what type or style they wanted,so i just replaced cables. as this is being used to join elecsa i was wondering how to phrase it in the departures and comments section,any ideas?
 
Comments "existing downlights retained in bathroom. Recommend replacing these for IP rated units"
 
i was wondering how to phrase it in the departures and comments section,any ideas?


Reminder.It is a comment on the "existing installation" and should be included at that place not as a departure
 
before recording it as a departure, measure the height of the ceiling. if it's over 2.25m, then t=it's out of zones, so not a departure
 