GLENNSPARK

found this today on a pre sort-out inspection:

Picture 048.jpg

all appears fine apart from the downstairs sockets not on the RCD side...split load board to the 16th ed

now lets pan down a bit:

Picture 049.jpg

yep...its TT...heres some more:

Picture 050.jpg

Picture 051.jpg

Picture 055.jpg

i wasn`t too impressed with the workmanship here either:

Picture 052.jpg

Picture 047.jpg

went into the bathroom..and found this:

Picture 056.jpg

oh, by the way...the DP switch in the pic is wired with the incoming on the outgoing...as the neon wont go off when the switch is opened.

and here`s a bit more from the bathroom:

Picture 057.jpg

i dont like the FCU and fanswitch where they are as its right next to the bath and the showerhead is a handheld one....
check out someones idea of a trunking job as well....lol...
 
Last edited by a moderator:
Hi,
Matey down the Pub sorted it for me , 50 Quid; would of been 60 for a spark so I've saved meself a tenner!

Regards.
well...it was a let..

so its a case of tite-arsed landlords R US..

together with Yarrick/Darrick to `lend a hand`...
 
Hi Glenn, where is that install, it looks very familiar, i am sure i have been introduced to it at some time a while ago, i seem to remember putting a quote in, and advising PME connection from DNO. I then heard nowt.
 
Hi Glenn, where is that install, it looks very familiar, i am sure i have been introduced to it at some time a while ago, i seem to remember putting a quote in, and advising PME connection from DNO. I then heard nowt.
well..
were going to drop another RCD in there for the unprotected ways...and sort out the bathroom crap as well Howard...

i will straighten out them cables thats coming down as well....
 
shocking. and from the last 2 pics it's obvious that willie the wet-head has struck with his defined scope.
 
shocking. and from the last 2 pics it's obvious that willie the wet-head has struck with his defined scope.
seeing it a lot Tel...more work for us..
but yep...its not good is it...
it needs to change does all this...
 
well..
were going to drop another RCD in there for the unprotected ways...and sort out the bathroom crap as well Howard...

i will straighten out them cables thats coming down as well....

I think it is where i went, i wont name the street but is it near the Co-op on hare hills lane?

You might need a RCD main switch if your Ze is that high.
 
what@s the black cable from cut-out through the wall?
 
it`ll be a shared suppy tel...
the paper-lead comes in here as can be seen...then splits out from the head to another service head next door...
i`v worked on loads of installs set up like this...
usually on the other side...lol..

both service heads will have 60A BS1361 type IIb`s in em...
 
well...it can have a 100mA s type as the main switch Howard....and another 30mA in there for the unprotected finals...
 
I think it is where i went, i wont name the street but is it near the Co-op on hare hills lane?

You might need a RCD main switch if your Ze is that high.
i`v forgotten the name Howard...but its a rite short street....late victorian terraced...
 