Well, I'm a little bit confused :rolleyes:
I have two circuit breakers, upstream CB is NSX630F (36kA Icu at 380/415 VAC 50/60), while downstream is IC60N (10kA Icu 220...240 VAC 50/60). They are in total dicrimination, BUT - IC60N cannot operete in cascading mode with NSX630F. WTF? o_O
 
When you say "cannot operate in cascading mode" do you mean that when cascaded you fail to meet the main supply PFC break requirements that you expected from the NSX630F?

When you have two OCPD in cascade the break limit is based on which one has to actually interrupt the supply, and perversely when you have "total selectivity" that becomes the smaller one!
 
When you say "cannot operate in cascading mode" do you mean that when cascaded you fail to meet the main supply PFC break requirements that you expected from the NSX630F?

When you have two OCPD in cascade the break limit is based on which one has to actually interrupt the supply, and perversely when you have "total selectivity" that becomes the smaller one!
No idea, ECOStructure told me that.
 
Cascading requires some action by the upstream breaker to limit the current that the downstream one would have to break, whether it is a momentary contact separation or actual triggering. Therefore any current >Icu at the downstream breaker needs to trigger that action. A breaker pairing that is not valid for cascade protection could allow a fault to occur that does not trigger current limitation upstream but cannot be broken downstream.
 
If I have for example upstream CB from ABB, and downstream from Siemens, how to know are they compatible for cascade protection?
I expect you would have to ask them, as it depends very much on the trip characteristics (i.e. if the upstream breaker is going to current-limit the fault with the downstream one).

It is usually easier with upstream BS88 (or equivalent) fuses - most companies give to the cascading / selectivity figures for that arrangement.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Zagreb
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
All Other Countries (This Is English Speaking Website Only - WE don't mind Google Translate Users :)
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Discrimination and cascading
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
Designmen90,
Last reply from
pc1966,
Replies
8
Views
1,729

Advert

Back
Top