Afternoon all, I'm just working on the design of a large commercial property and they have requested external lighting, Which I have split into 3 areas, Back of house (deliveries, storage etc) Customer car park and staff car park area. I've got the lighting sorted to the requested levels which Is effectively my job over due to the nature of this job ,But I'm now wondering how It all gets distributed as I have very little knowledge of street lighting and the such.
My assumption is that from the main switchboard within the installation a feed gets taken to the external feeder pillar, in the pillar is a small 3ph DB for a few bits of external power, and then the DB/timeclock/controls for the lighting, set up just like a standard DB, Which would feed out to the lighting columns, Which would have a cut out within each column.
Am I on the right track or way off? It's not something I've had a lot of experience with.

Thanks in advance.
Jim
 
Most street light circuits I do would be as a ring main, and a good rule of thumb is a 16mm ring.

Remember when you calculate your VD you do it is sections so Panel to first light will be the total load, then a-b will be total load minus first first lamp etc etc, and you then add up the indiviual VD of each section to get the total,you can google the formula no doubt.

Also if your using typical lamp post columns and SWA 9 time out of 10 then will not be anywhere to terminate a SWA gland. Use the banjos with the lock nut and join the banjos with a brass 6mm nut, bolt washer and fly earth onto your fuse carrier/MCB holder
 
Most street light circuits I do would be as a ring main, and a good rule of thumb is a 16mm ring.

Remember when you calculate your VD you do it is sections so Panel to first light will be the total load, then a-b will be total load minus first first lamp etc etc, and you then add up the indiviual VD of each section to get the total,you can google the formula no doubt.

Also if your using typical lamp post columns and SWA 9 time out of 10 then will not be anywhere to terminate a SWA gland. Use the banjos with the lock nut and join the banjos with a brass 6mm nut, bolt washer and fly earth onto your fuse carrier/MCB holder



Or you could use a central earth terminal in the colum, they are designed for street lighting.
 
Last edited:
Thanks for the input guys, all interesting stuff, I didn't know about the alternative volt drop calc Malcolm How come it's different?
Am I correct in thinking each individual column has its own cut out, and then that circuit is backed up by a breaker of some sort.
 
Thanks for the input guys, all interesting stuff, I didn't know about the alternative volt drop calc Malcolm How come it's different?
Am I correct in thinking each individual column has its own cut out, and then that circuit is backed up by a breaker of some sort.

For any circuit feeding multiple fixed loads you would calculate each stage separately for VD otherwise you end up with massive cables unnecessarily
 
Thanks Davesparks, thought that might be the case, Ive never heard of a different system being used before.

I was looking at them earlier Flanders, they've got quite a helpful website for idiots like me :dizzy2:
 
Thanks for the input guys, all interesting stuff, I didn't know about the alternative volt drop calc Malcolm How come it's different?
Am I correct in thinking each individual column has its own cut out, and then that circuit is backed up by a breaker of some sort.

Hi

The method Malcolm sugests is suitable for a radial, a ring is a litlle different, you need to use kirchoffs current law,

Different parts of the cable will see differing levels of current dependent upon topology and load distribution.

As a rule of thumb, if you wire in a ring add a factor of 0.25 to th VD equation, if its a radial circuit factor is 0.5. If lighting is evenly distributed it will give very close results.

Cheers
 

Reply to Distributing external/street lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I am drawing up a contract for a job in a domestic property which has a 3-phase Distribution Board and need to supply 3ph to a heat pump that's in...
Replies
3
Views
2K
This might be long so feel free to grab a brew. So, as some of you may know, i'm a 34 year old who has been dying to get into the industry. I...
Replies
66
Views
9K
Hi looking for some advice Guy at work has been jointing existing street light feeds to be fed from another position, now he’s connected at the...
Replies
9
Views
2K
Good morning hope everyone is staying safe. I have a question for some of the more experienced sparks, I have a client that wants her outdoor...
Replies
2
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock