Simple answer:
No.
Temperature, climatic conditions and air bourn contaminates all add together.
I had samples of 50 year old VIR SWA tested as part of a modernisation project. The MCC panel was replaced, the cables reused. The cables were in perfect condition due to the cool and stable environment.
.....'Degradation' is a very unfocused term. Materials degrade in many ways therefore degradation can be measured in many ways such as durability(how brittle), discoloration, porosity etc but I guess in this context the main concern would be dielectric strength.
I doubt the relationship between the dielectric performance and time would be linear, most of these types of failure curves are somewhere between linear and logarithmic where degradation accelerates ever more rapidly in the late stages leading up to catastrophic failure.


'Degradation' is a very unfocused term. Materials degrade in many ways therefore degradation can be measured in many ways such as durability(how brittle), discoloration, porosity etc but I guess in this context the main concern would be dielectric strength.
I doubt the relationship between the dielectric performance and time would be linear, most of these types of failure curves are somewhere between linear and logarithmic where degradation accelerates ever more rapidly in the late stages leading up to catastrophic failure.
Yes pulled out a lot of 7029 pvc just as good as when it was installed, cant say that with vir in my experience.