It is a new Reg in the 18th Ed draft, 10% of the rated residual operating current of the device.

Thanks for that westward. I've checked your post #30. That's interesting to know.
I've now got my books out( 17th edition that is) and I still cannot find where I've think I've seen 25% of rated residual current as a design guidance. Therefore a 30mA rcd should be designed with7.5mA as its max.
I know I've seen it somewhere.

I'm wandering where the 30% 9mA came from.
 
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.
 
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.

Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.
 
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.

Really .............. not sure I believe that.

So how do you estimate the anticipated earth leakage of any device then?
 
Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.
I am only quoting a rule of thumb I believe may be quoted in a commentary/guide book which is what Paignton Pete has probably seen and stuck in his mind. 25% equates to 7.5ma for a 30ma device and it does ring a bell in my head that this should be used as a basis for circuit design. It may have some substance with the proposed 18th Ed quoting 30%.

Edit, see #57.
 
Last edited:
Thanks for that westward. I've checked your post #30. That's interesting to know.
I've now got my books out( 17th edition that is) and I still cannot find where I've think I've seen 25% of rated residual current as a design guidance. Therefore a 30mA rcd should be designed with7.5mA as its max.
I know I've seen it somewhere.

I'm wandering where the 30% 9mA came from.
Okay this is bugging me so if you have a 16th Ed copy with Section 607 in it check out Regulation 607-02-03 there you will find it.
 
I'm sceptical about that much leakage current flowing in a healthy circuit too, unless there's a heck of a lot of I.T. equipment all going at once.
 
Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.
The aim here is to keep the currents at a happy level to prevent unwanted tripping, ideally an rcd/rcbo should trip under fault conditions and not excessive leakage when there is no fault. By quoting a percentage level you allow some leeway for further accumulated current and all should be good. Design a circuit where levels are excessive then any further accumulated current may result in unwanted tripping.
 