Maybe you've been abroad too long as Sussex is south coast....a long way from the broads!. My area has sandstone,chalk and clay regions.....the clay seems to be most consistant as far as Ra values go. But I am quite truthful when I state that none of the TT installs I encounter around here are anything like the TT installs which everyone claims to be installing.


Your right, i must have been out of the country far too long, getting confused with Suffolk/Norfolk area ...lol!!

The closest i've ever driven a rod to you, was for an uncle in Broadstairs Kent (along the same coastline). Can't remember what the final Ra was now, but as i remember, it was more than acceptable.

Have you ever tried soil conditioning on any of you're TT installs?? A little while ago i posted what i thought was a good idea for any electricians that deal with a lot of TT installs. It centres around buying a relatively cheap fence post auger, extending the shaft on a 75 mm auger bit to around a metre or so and using this go down a metre into the soil Fill the excavated section with Bentonite slurry and then driving in two or more 1.2m rods (or one 2.4m rod etc). This will almost guarantee you a very low Ra...
 
Your right, i must have been out of the country far too long, getting confused with Suffolk/Norfolk area ...lol!!

The closest i've ever driven a rod to you, was for an uncle in Broadstairs Kent (along the same coastline). Can't remember what the final Ra was now, but as i remember, it was more than acceptable.

Have you ever tried soil conditioning on any of you're TT installs?? A little while ago i posted what i thought was a good idea for any electricians that deal with a lot of TT installs. It centres around buying a relatively cheap fence post auger, extending the shaft on a 75 mm auger bit to around a metre or so and using this go down a metre into the soil Fill the excavated section with Bentonite slurry and then driving in two or more 1.2m rods (or one 2.4m rod etc). This will almost guarantee you a very low Ra...

No I havent tried soil conditioning....and nor have I encountered any other installs where this is apparent.
Oddly I had another Ra issue yesterday.....on a roof extension to a terraced property which was a TT. Final testing on completion showed an Ra of over 300 ohms. Two coupled rods got it to 24. At the moment there is an existing DB with RCBO's and a main switch,am currently trying to convince the owners to swap the M/S for a 100ma s type.
 
Final testing on completion showed an Ra of over 300 ohms. Two coupled rods got it to 24.

Wow, you guys have no idea how lucky you are, I wsh we got those kinds of Ra's with just two coupled rods.

In six months or a years time your new rod will probably be down to 15ohms so it does beg the question why was the original rod such high impedance?
 
Wow, you guys have no idea how lucky you are, I wsh we got those kinds of Ra's with just two coupled rods.

In six months or a years time your new rod will probably be down to 15ohms so it does beg the question why was the original rod such high impedance?

The original rod was located 6" from where two DNO cables dropped into a duct in the ground,the original installer had bottled it and only gone in about 2.5 ft! We shifted the electrode position well away from any services.
 
the original installer had bottled it and only gone in about 2.5 ft!

You can't be serious!! They need to start including a minimum required depth in the regs me thinks. I also can't believe he got 300ohms at that pitiful depth. You must have superb ground for earthing and it makes me depressed just hearing things like that, I've had two separate spikes at over 8m deep and not got 300ohms on more than one occasion :(
 
You can't be serious!! They need to start including a minimum required depth in the regs me thinks. I also can't believe he got 300ohms at that pitiful depth. You must have superb ground for earthing and it makes me depressed just hearing things like that, I've had two separate spikes at over 8m deep and not got 300ohms on more than one occasion :(


Ah, but you have told us on a few occasions, that the base soil is almost deep pure sand in your location. That sands sulphates and chlorides content has also been probably washed/drained away too, by the sounds of it!!
 
I installed a rod this week for a customer who's existing TT was via the water pipe (140 Ohms). The meter is in the middle of the house and the kitchen ceiling was down so that was the obvious route to a bit of 6" thick concrete outside, I would have preferred to go further into garden but customer was not happy about disturbing decking and paving.

Got square of concrete out, fitted earth pit, filled pit with slurry of bentonite and started hammering.

After 2 X 4ft rods got 70 Ohms, after third rod got 40 Ohms. At this point having run out of rods I stopped to consider options. Problem is how do I justify going further and spending more money to customer?

While I would like to go for a lower Ra adding another rod is only going to get it to about 20 Ohm unless something in the soil makes a big difference 12ft down. Unless I can get it down around 1 Ohm is having 20 Ohm vs 40 Ohm going to make any difference as it will still be reliant on the RCD. Adding another pit is a no go for customer.

Comments welcomed.

PS. Ze of 31 Ohm with water bonding connected.
 
Last edited by a moderator:
I installed a rod this week for a customer who's existing TT was via the water pipe (140 Ohms). The meter is in the middle of the house and the kitchen ceiling was down so that was the obvious route to a bit of 6" thick concrete outside, I would have preferred to go further into garden but customer was not happy about disturbing decking and paving.

Got square of concrete out, fitted earth pit, filled pit with slurry of bentonite and started hammering.

After 2 X 4ft rods got 70 Ohms, after third rod got 40 Ohms. At this point having run out of rods I stopped to consider options. Problem is how do I justify going further and spending more money to customer?

While I would like to go for a lower Ra adding another rod is only going to get it to about 20 Ohm unless something in the soil makes a big difference 12ft down. Unless I can get it down around 1 Ohm is having 20 Ohm vs 40 Ohm going to make any difference as it will still be reliant on the RCD. Adding another pit is a no go for customer.

Comments welcomed.

PS. Zs of 31 Ohm with water bonding connected.

Go back and check it again this time next year, you maybe pleasantly surprised that your value has fallen substantually
 
you can take consolation in the fact that mid july is hottest time of year and the ground wont get any dryer , thus the readings wont get any higher.
test the rod between oct-april , when damp /wet , it will likely be below 50 ohms.

silver linings and all that :-)

^^ in reply to the OP
 
Sounds like it's time the 'powers to be' stop dicking around with vague comments in the BGB and give more specific guidance on what they want to see from TT installs - if they can ever agree!
 
Sounds like it's time the 'powers to be' stop dicking around with vague comments in the BGB and give more specific guidance on what they want to see from TT installs - if they can ever agree!

The whole section badly needs updating, as it stands it's a bloody farce!!
 