Openroad

I am replacing my present double oven with two seperate ovens. Fan oven, 2200w max and an integrated combi micro, 3100w max (no plug).
The present 32A supply is adequate for both, but do I need two separate supplies direct from the CU, one for each oven?
 
A 32 A final circuit is usually appropriate for household cookers of a total rating up to 15 kW.
OSG Appendix 8.4 gives the following guidance:
"A circuit of rating exceeding 15 A but not exceeding 50 A may supply two or more cooking appliances where these are installed in one room. The control switch or cooker control unit should be placed within 2 m of the appliance, but not directly above it. Where two stationary cooking appliances are installed in one room, one switch may be used to control both appliances provided that neither appliance is more than 2 m from the switch. Attention is drawn to the need to provide selective (discriminative) operation of protective devices as stated in Regulation 536.2."
 
Last edited by a moderator: