OK since all is quiet, I would purchase a wylex 108M and a 60 or 80A fuse to protect your submain (dependant on reference method), Move the isolator up put the Switchfuse below it and tail into that from isolator, then take your armoured straight into the switchfuse as it will be metal, I would say it would be perfectly acceptable to your DNO to have a suitable switchfuse mounted in their meter box