IMG_20130523_183230_0.jpghi need help please ,im useing swa 3core from this main dp isolater back to the metal/ consumer unit,my q is how do i terminate the swa at the dp isolater,many thanks
 
Thinking about it though, will you need to fuse your submain? (answer almost certainly yes) ;-)
 
OK since all is quiet, I would purchase a wylex 108M and a 60 or 80A fuse to protect your submain (dependant on reference method), Move the isolator up put the Switchfuse below it and tail into that from isolator, then take your armoured straight into the switchfuse as it will be metal, I would say it would be perfectly acceptable to your DNO to have a suitable switchfuse mounted in their meter box
 
Personally i'd say that isolater wasn't DNO property and was only installed for ease of self connection and so that they can walk away with the meter sealed.

I would remove it and put the tails straight into your switch fused. Move that earth as well to give you all the bottom right corner.
 
thanks for the help av1 need to go and see if i have space for the
wylex 108M ,i think i would go for somersetsparks idea. thanks again,
 