Discuss Dual RCD's in the Australia area at ElectriciansForums.net

Reaction score
25
At College,haven't covered much yet about dual RCD's
What is the advantage of using two Rcd's over one.
What circuits would be on each section of the CU?
Also I have an old re wirable type CU and am thinking of changing it(with more knowledge).
I have a split load board with one Rcd would this be suitable for my terraced house,would it comply with the Regs?

Sorry,so many questions,so little time.

Any help with some or all of the answers would be greatly appreciated

cheers Gerry
 
The 17th Edition requires most if not all circuits in domestic premises to be RCD-protected. There have been a number of suggestions as to how the consumer unit may best be configured to comply with the Regulations, the most common being a main switch with
RCBOs
protecting each individual circuit. However, another suggestion favours a main switch with two
RCDs
protecting separate DIN rails. If careful consideration is given as to what each bar will control in the way of upstairs and downstairs lighting and power circuits, will this configuration comply?

NDA2
Yes, as long as the division of final circuits between the RCDs is carefully considered so as to minimize the consequences of unwanted tripping. Separate RCD protection is not necessarily required for each circuit of an installation but, in order to minimize the likelihood and consequences of tripping, a single (‘front end’) RCD should not be used to protect all the circuits.

What it means is if you have 1 RCD protecting all circuits and one of the circuits develops a fault , this will trip the RCD and cut power to all circuits , which is what they are trying to avoid .... if you split the circuits over 2 RCDS if you have a fault on one of the rcd the other should not trip , meaning the you still have 50% of your circuits working .... which means you don't have total black out..... Hope this make sense , as it does in my mind :D
 
RCD's are ONE way of protecting cables buried less than 50mm from the surface of a wall/partition.


However, there are now requirements to RCD protect all circuits in a bathroom, all socket outlets etc.

So, Dual RCD boards are a cheaper then loading a CU with RCBO's, some of which can cost up to £30 each.

If you have a look in the OSG or the BRB it lists all the other options to avoid them, circuit permitting, Eg use of earthed steel conduit, surface wired etc.

So, in answer to one of your questions, no, a standard split load board will not meet current regs, unless you load the unprotected side with RCBO's.
 

Reply to Dual RCD's in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
447
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
791
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock