Good question, I have done several new school Kitchen builds over the last 3-4 years and always bond the furniture in there due to 3 phase table top dishwashers and also waste disposal units under sinks etc and also some have electric ovens and there are lights and fans in the canopies above, although they don't touch the furniture the staff can have their bodies against the tables and be touching controls for fans so I do it as norm myself, some of the little metal tables on wheels I don't bother with but right or wrongly I do earth, Thats just me.
 
Old 15th edition Regs, which were abolished later on. So no need to bond the stainless steel work tables these days. in fact anything that has a value when tested of 23kOhms or above...
 
Yeah I loved the 15th, bonding of patio doors, false ceilings and anything metal, loved it haha, JK, I did say right or wrongly, I would still bond the furniture in a school with electric appliances sat it, Just what I would do, doesn't cost much and no big hardship doing it either on a commercial scale price wise.
 
IMO , by bonding the tables you make the installation less safe as a person touching the table/s would then be well earthed and as such any shock received could be fatal. TIN HAT SECURELY ON.
 
just a thought though if the sockets were just o an mcb and not rcd protected would that change the sittiuation
well....i would then....look at a schedule of inspections under additional protection...RCD or supplementary bonding....
 
IMO , by bonding the tables you make the installation less safe as a person touching the table/s would then be well earthed and as such any shock received could be fatal. TIN HAT SECURELY ON.
but the same could be said for tiled walls Tel.....damp?...
 
OK, but wet is not as good a conductor as steel. and they're more likely to be touching a table than the walls. i,m thinking of the scenario that started the part p fiasco, where she was earthed by her leg being in contact with the casing of a dishwasher.
 
OK, but wet is not as good a conductor as steel. and they're more likely to be touching a table than the walls. i,m thinking of the scenario that started the part p fiasco, where she was earthed by her leg being in contact with the casing of a dishwasher.
i agree that theres times when just indiscriminately earthing something can in fact introduce a potential....so i guess it would go on the individual scenario....
 
i`d probably just consider the re-heat age dinner ladies as unskilled/uninstructed persons anyway....and so....
 
IMO , by bonding the tables you make the installation less safe as a person touching the table/s would then be well earthed and as such any shock received could be fatal. TIN HAT SECURELY ON.

agreed.
what electrical potential does a metal table introduce exactly ?
is it extraneous ? is it exposed conductive ?
of course it bloody isnt.
and 3 phase / non rcd has nothing to do with it.
catch you doing it on my jobs and i'll be walking round with my snips , grumbling incoherently.
 
IMO , by bonding the tables you make the installation less safe as a person touching the table/s would then be well earthed and as such any shock received could be fatal.

Yes the bird on the wire situation, you could say the same about bonding pipework in houses as well I suppose, interesting conversation, I know engineer is right saying there is no need and it is 15th edition , I still see no harm myself though but there we are.
 
I still see no harm myself though but there we are.
However, the fact is that there is harm in it.

Bonding is applied because a part is already earthed.

Earthing (it would not be bonding) isolated parts introduces a hazard.
 