Engineer54
But this assumes that anything approaching 200 ohms IS going to be unstable...the fact is it isn't....why should 200 ohms be any more unstable than 30 ohms?
As I've stated on here before I've tested and installed many 'useless twigs' in my area over many years and typically get readings of between 100 and 150 ohms summer and winter.Some have been on installs which have had regular updates and alterations over long periods and so have had regular Ra tests,if I have found dangerously unstable Ra readings believe me I would be doing something about it.....but I haven't. And many of the "it's got to be 20-30 ohms" brigade seem to forget that 30 ohms or 200 ohms they are still totally reliant on an RCD to meet disconnection times
Of course if in your ground you cant get a stable Ra with a 'twig' then don't use one....but to state across the board that standard UK rods are never going to be adequate or stable is wrong.
I am plainly stating that a single twig sized so-called earth rod, is basically useless, no matter what the inital Ra value is, i'll stand by that statement come what may!! I honestly can't see how your not seeing seasonal differences with such twig's, i would go as far as saying it would be almost impossible Not to see drastic seasonal differences... Not only that, a TT system should be suitable for a 30 year life span, but most will still be in service 50 or 60 years. Anyone that thinks these twigs are suitable or i suspect even designed for such durations are only fooling themselves. The only use i can see for these twigs, is for a very temporay install, or as re-usable test rods for an earth tester!!
Any domestic TT system should minimally consist of at least 2 X 5/8'' rods coupled together wherever it's possible to drive them. On commercial and/or industrial installations of any size, a far more concerted effort should be made to get a good working TT system. I will agree, that there are certain times that due to the ground conditions you can be hard pushed to better a stable 200 ohm value with driven rods. Depending on the installations requirements, even these TT systems can be substantually improved. I'm not saying this would make sound economic sense on a domestic installation, but it can for other installations...
Perhaps if these short rods of any size were never brought on to the market and you were still using the older 6 and 10 foot rods, we wouldn't be having these debates!! As in those day's 10 ohms was what the electricians were looking for, certainly not 200 ohms or anywhere close. What's more, in my old county of Essex you would feel unlucky if you saw an Ra 10 ohms, it was generally much lower!! And here you are telling us all, of the benifits using these 3'8'' twigs and of drawing the line at 200 ohms or so. Thank god that most water/gas services are still metallic and can give much needed support to these numbty twigs and values that you can't see any problem with....