S

spark-ticus

Please excuse my ignorance my professional comrades but i am completing a schedual of test results and am not sure of the earth size in 1.5mm, 2.5mm an 4.0mm cable. If someone would be so kind as to enlighten me i would be very gratefull and promise to thank you with a click of the thank button!!!!!
 
Please excuse my ignorance my professional comrades but i am completing a schedual of test results and am not sure of the earth size in 1.5mm, 2.5mm an 4.0mm cable. If someone would be so kind as to enlighten me i would be very gratefull and promise to thank you with a click of the thank button!!!!!
are these test results part of a college exercise?...or for an actual install?......
 
Standard T+E Sizes:
Line (mm[SUP]2[/SUP]) CPC (mm[SUP]2[/SUP])
1 ------------1
1.5 ----------1
2.5 --------- 1.5
4 ----------- 1.5
6 ----------- 2.5
10 ---------- 4
16 ---------- 6

Note: Be aware up to 3 CPC size options are available from the cable manufacturers for most T+E cable sizes, however, mostly encountered in commercial or industrial installations.
OSG Appendix I, Table 11.
 
Last edited by a moderator: