Iwas just wondering if anyone could tell me what sort of earth system the following scenario would be.
Large commercial premesis with own supplier transformer
Incoming earth to met straight from transformer
several eart electrodes around building to met bar

Many thanks
 
Evening Gents

Iwas just wondering if anyone could tell me what sort of earth system the following scenario would be.
Large commercial premesis with own supplier transformer
Incoming earth to met straight from transformer
several eart electrodes around building to met bar

Many thanks
when you say `incoming earth straight from transformer`...is this a sheath earth or neutral earth?

- - - Updated - - -

if neutral earth then likely to be PNB....
 
got that wrong pnb is tns never heard it called that before whereas pme is the term for tncs
many thanks
I thought it would be tns but had never worked or installed on a buiding with its own transformer and wasnt sure if the fact they are combined at transformer meant it was tn-c-s suppose even tns is combined at transformer anyway.
Thanks
 
Virtually all TX supplied site/factory/project installations will be TN-S..

More likely that the N-E connection for this distribution TX will be located at the main switchboard. This facilitates the TX restricted earth protection relay CT's etc. And yes, all TN-S systems start life as TNC-S...
 