ample current

I have been working in a house and replace a couple of power circuits and when I was determining the earthing arrangements I traced the main earth to an MET right next to the service head (MET is slightly unsighted due to its position in the cupboard). the earth cable then continued from the MET out through the wall to an earth rod by the front door. I assumed a TT. When I checked the ZE it came out to read 0.41 ohms. now have I missed something and its TNS arrangement with an earth rod still connected. The supply cable was in a tube and the service head placed immediately on top of the tube containing the supply cable so impossible to see if it had an earth cable attached.

any comments would be appreciated.
 
did you measure Ze with the bonding dissed, or directly to a dissed earthing conductor?
 
I disconnected the earthing conductor from the fuse board (to remove parallel paths) left the MET in place (nothing else was connected to the met) and cable connected to the earth rod and measured Ze in the usual manner
 
Sounds like it was TT at some point and cable was left in, or an electrician wasn't sure and rodded it. Can't see it being TT now with 0.41 (not unless Eng54 did it :) )
 
to the O/P:

why oh why do we get thick threads like this?

of course its not chuffin TT...not with a Ze of .41...use your sense man

beggers belief...
 
to the O/P:

why oh why do we get thick threads like this?

of course its not chuffin TT...not with a Ze of .41...use your sense man

beggers belief...

Although i'd agree with you here 99% of the time, i can show you house TT Ra values in salt marsh areas of Essex, that are more than comparable too this value, ...achieved with a single 3m rod!!
 
Although i'd agree with you here 99% of the time, i can show you house TT Ra values in salt marsh areas of Essex, that are more than comparable too this value, ...achieved with a single 3m rod!!
OK...fine...

but that wont be the case here...it`l be a TN-S...
 
And,if he is working where he lives,it may be a similar salty conductive paradise to ENG's example :thinking:
 
well whatever it is...its already boring the hell outa me is this thread...

why dont the O/P use his senses (eyes in this case)....go and verify it for himsen ..

rather than expecting us to be able to verify it for him....

bloody waste of time if you ask me....
 
This thread dis make me chuckle a bit. As though we can be sure of anything whilst sitting on out backsides at home. It's clearly likely to be a TN-S system, but only the OP can verify this.
 
If its the type of rod I am thinking it is, installed tight up to the brickwork of the house with about 4 inches exposed in clear air, every one I have ever found has been taken out of service many decades ago.
 
If its the type of rod I am thinking it is, installed tight up to the brickwork of the house with about 4 inches exposed in clear air, every one I have ever found has been taken out of service many decades ago.

Many decades ago electricians tended to drive/use 10 foot earth rods or 3/4'' galv water/gas pipe. But then again in those days, they weren't working to the present 200 ohm Ra, they were working to 10 ohms!! It's these day's you're more likely to see short thin twigs (that weren't around decades ago) installed tight up against house walls.
 