Ian B
~
I can't publish them here as they are copyrighted documents, but COP-3 is available from here: CAI Publications
Assuming they are above the flat areas absolutely.Well that link isn't going to tell me much ..lol
I'm only talking about the situation where a LP system is in place. Any dish or antenna's framework, will need to be connected to that LP system, as they will both extend beyond the protected flat areas and be acting as an ''air conductor'', there is no if's or but's about that!!
No I'm saying the CAI COP states that the dish/mast should be connected to the MET via the equipotential bonding system at the headend using 4mm conductor if the building has a LPS fitted, whether or not the LPS is connected to the mast/dish.Now if your saying that a separate 4mm CPC should also be taken from these dish frames/structures to the MET direct, you are effectively cross connecting and negating the LP systems protection and allowing a lightning strike passage direct to the installations MET!! ...Rather you than me ...lol!!
Agreed, the purpose of the 4mm connection is not for LPS.All your head and other hardware stuff can be effectively protected in such LP systems by the inclusion of surge arresters...
There's no 'conflict'. The LPS will provide an 'easier' path to ground for LP, and the equipotential bonding will prevent circulating earth currents in the signal cabling, however feel free to take it up with the CAI if you wish.Let me assure you that in the hundreds of LP systems i've been involved with, i have never connected or seen any dish/antenna frames directly connected to a MET, where it is protected by the LP system. It is if you like a conflict of interest between the two earthing systems..
Assuming they are above the flat areas absolutely.
No I'm saying the CAI COP states that the dish/mast should be connected to the MET via the equipotential bonding system at the head end using 4mm conductor if the building has aLPS fitted, whether or not the ALPS is connected to the mast/dish.
Agreed, the purpose of the 4mm connection is not for LPS.
There's no 'conflict'. The LPS will provide an 'easier' path to ground for LP, and the equipotential bonding will prevent circulating earth currents in the signal cabling, however feel free to take it up with the CAI if you wish.
:cool4:
This is possibly true as in the BS it states that LPS systems should now be connected to the MET, a practice that I really don't agree.