Search for tools and product advice,

Discuss Earthing in the Electricians' Talk | All Countries area at ElectriciansForums.net

S

Sparkii

Hey guys,

I'm looking at a job just now and im a little unsure about the main bonding of incoming services. At the moment it's a large industrial unit and the plan is to make 11 smaller units that will be rented out. Each will have it's own 3ph board supplied by 40A isolator, gas meter and water meter. Do i need to bond the services in each unit from each DB, or would an earth from the main earth bar to the services as they enter the building be sufficient? All pipework in the building runs through each unit at high level and drops down to the individual meters

Thanks in advance
 
If these industrial units have it's own DB and are completely separated by the fabric of the building, then Yes, you will need to conduct a bonding exercise at each unit. The Units should be considered as you would in a block of flats, where exactly the same situation exists, with common service pipes branching and entering each dwelling....

If the building is a steel framed building, then you may use the steel frame of the building to bond out these services, and the Individual Unit DB's. But as the pipes enter the building, they will still need to be bonded by a copper conductor as well as the buildings structural steelwork to the main switchboards MET...
 
Last edited by a moderator:

Reply to Earthing in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
952
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
947
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
804
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock