Looking for some input/opinions on a recent EICR resulting in a C2 for a consumer unit.
Current conditions are plastic CU, in good condition, no damage, no faults, all MCB and RCDs (not RCBOs) in good working order.
The premise is a rented flat.
It is 5 years since the last one where this was not cited as an issue.
Why would this warrant a C2?

Thanks
 
What is the exact wording for the C2?
Thanks for the response.
I will have to ask the lady.
But I understand it is the same as you see on that quote.
She rents out a part of her home to supplement her pension.
So she's a bit alarmed by the requirement.
She asked me and I can't think of any reason why this is deemed necessarry.
It's a different inspector to the one who did the last EICR.
I have offered to speak to the inspector directly but she's a bit nervous about me doing so.
I will see if she can send me a scan of the report.
 
Thanks for the response.
I will have to ask the lady.
But I understand it is the same as you see on that quote.
She rents out a part of her home to supplement her pension.
So she's a bit alarmed by the requirement.
She asked me and I can't think of any reason why this is deemed necessarry.
It's a different inspector to the one who did the last EICR.
I have offered to speak to the inspector directly but she's a bit nervous about me doing so.
I will see if she can send me a scan of the report.
if you have a Look at Electrical Safety Guide 4 issue 7.3 ( downloadable) I think you will find it is not a C2.
Thanks for the response.

I have read that document and it is a high level summary of the A4:2026 amendments without specific details.
It doesn't mention anything with regards to whether these amendments are retrospective.
They haven't been before to the best of my knowledge.
I have the big yellow version 17th Edition BS7671:2008 which is getting on a bit now.

"I think you will find it is not a C2."

How exactly do you come to that conclusion?
The property owner tells me that it is classed as a C2.
I haven't seen the actual report mind you.
All she did was send me the quote.
I have asked her for a copy of the report.
I am still waiting.
 
Thanks for the response.

I have read that document and it is a high level summary of the A4:2026 amendments without specific details.
It doesn't mention anything with regards to whether these amendments are retrospective.
They haven't been before to the best of my knowledge.
I have the big yellow version 17th Edition BS7671:2008 which is getting on a bit now.

"I think you will find it is not a C2."

How exactly do you come to that conclusion?
The property owner tells me that it is classed as a C2.
I haven't seen the actual report mind you.
All she did was send me the quote.
I have asked her for a copy of the report.
I am still waiting.
There's really not much to go on until you see the EICR. Hopefully they have been very clear about why it's a C2. You can't really form any decision based on what the lady has said.
 
Looking for some input/opinions on a recent EICR resulting in a C2 for a consumer unit.
Current conditions are plastic CU, in good condition, no damage, no faults, all MCB and RCDs (not RCBOs) in good working order.
The premise is a rented flat.
It is 5 years since the last one where this was not cited as an issue.
Why would this warrant a C2?

The fact that flat is rented is an important consideration as is the position of the unit ( under a stair perhaps). Ultimately it is a matter of professional experience and judgement of the electrician.
 
There's really not much to go on until you see the EICR. Hopefully they have been very clear about why it's a C2. You can't really form any decision based on what the lady has said.
Thanks for the response.

I have just noticed that the image I posted with the original posting has disappeared for some reason.
Or not uploaded in the first place.
I am unable to post images apparently.

But here is the gist of the C2

Replace Consumer Unit with Surge Protection and RCBOs.
Replace Downlights in Kitchen with Fire Rated Lights.
Blank Socket near Kitchen Sink.
Re-Test and issue new Installation Certificate.

A quote of £840.00

I have asked her to send me a scan of the report.
Still waiting.
 