EICR - Unsatisfactory

Hi,

I am about to get an EICR done on a residential property. If a cooker isolation switch is less than 300mm from the hob will this produce an unsatisfactory.

Thanks.
 
I would expect it to get an advisory c3, this is part of building regs. as long as it's not above the hob or in a really awkward position.
 
Thanks Steve. The switch is to the left of the Hob as in the attached pic.
 

Attachments

  • CIMG4105.JPG
    CIMG4105.JPG
    76.3 KB · Views: 99
Unless it’s directly behind the hob , I wouldn’t even code it

if it was behind the hob then c3
 
even then, a change of isolator to one with no socket would fix that.
Are there any 32A/45A isolators that are "landscape" orientation in a 2G back box? Obviously there are loads that are "portrait" but the only ones I've seen that are landscape have a 13A socket with them. Fitting one of the standard ones on its side seems a bit, well, badger's.
 
Never seen one, but google unearthed this single pole Clipsal switch from Rexel in Australia. Maybe they were having the same problem and a manufacturer decided to plug the gap in that market...

First thought was a grid plate, but never seen a 45A grid switch either.
 
But without the socket, it was late and I was tired so did not read the whole thread, still it's nice looking.
 