Discuss EICR's-Unrealistic expectations in the UK Electrical Forum area at ElectriciansForums.net
Deleted member 9648
For some time I have been concerned with the unrealistic expectations many punters have on what an EICR can achieve. A particular concern for me, as someone who carries out a lot of EICR's, is that this forum tends to perpetuate that expectation. Many threads offer advise to have an EICR carried out, good advise.....but all too often the line..."An EICR will find any issues with your installation" finishes the post. All too often we read...."an EICR would have picked that up", or "....why wasn't that picked up on an EICR".
Well maybe it would, or maybe it wouldn't.
Lets be clear, on all but very small installations an EICR will only involve removing a percentage of points for inspection, that is standard practice. Typically around 25%. That means 75% of points wont be removed for inspection. So a 1.0mm feeding a twin socket will not be noted if that socket is one of the 75%. There is very good reason for taking a percentage. First the cost and disruption burden would be unacceptable if every item and all wiring was inspected, and secondly the more an installation is disturbed the more likely it is the inspector will introduce faults not previously present.
I have had two instances recently of unrealistic expectations. First was a call from an EICR client complaining that a N load connection on an FCU serving an external pump installation had burnt out, the attending engineer said the fault should have been picked up by myself. The EICR was carried out 18 months ago and the pump had been fully working up till now!!
A second instance was at an IT company, I had arrived to install some sockets, but on isolating the circuit it was found a voltage of 180v N-E was present preventing work proceeding. Not sure what was going on as they decided to abandon the work rather than investigate. But an EICR had been carried out just a month ago (not by me), straight away indignation and threats of lawsuits etc.
They let me see the paperwork, a detailed and well compiled EICR. Clearly there were problems with isolating stuff in a large IT company, and the EICR clearly stated that each DB had been isolated for a limited time, where possible IR tests had been conducted, and then the DB was re-energised and Zs tests carried out on final circuits. That was all that was realistically possible in a company on-line 24hrs. But as final circuits were not individually isolated the above potentially dangerous fault went undetected.
The crux of the matter? When recommending an EICR can we please be realistic. It is NOT going to find every issue.
I suggest..." An EICR would be a good idea, whilst it cannot identify every issue it will give you a good indication of the general condition of your installation, and should highlight any potential dangers and whether remedial work or further investigation is required."
Sorry for the long post but I honestly believe we are creating a rod for our own back.
I drifted off about half way through WP! :)
I consider any technical business from an engineering point of view, it's a comprise between the ideal solution and cost.
If you want to 100% inspect, it's your time and client's cost. Plus, the old question, are you introducing faults on an otherwise OK system.
It certainly isn’t all it seems to be behind the pretty exterior - I did an EICR today where because it was empty 3 bed and the workmanship so shoddy with earthing on lighting missing etc I checked 100% as I was changing the board as well - still got stuffed with a faulty leg causing me an issue - my time and clients money!
Oh and the 10mm cooker circuit didn’t go anywhere so I’ve told the customer to carefully take the kitchen cabinets down for me so I could trace it next week (well, they were sticky!)
the EICR is like a car mot ,if a fault arise after you have done it ,then it is not your fault you can test and test till the cows come home .
we are not robots and plug in and see in the full system ,like dater from star treck.
A good post and interesting points @wirepuller. Yes in many ways you are stating the obvious but it is obscured by the fact that we all know the cost of really going through an install with a fine tooth comb will rule that out from the clients side at least. One of the things/solution? it made me think of was infra red cameras. If we used one on all fittings/terminations you may well have picked up the loose N you alluded to and perhaps other faults.
As far as the 2391 teaches we should not disassemble or at least keep it to the absolute minimum. Which militates against being thorough. Then a cross draft to that is EICR is about inspection much more than than testing and poking inside. I think the one thing I would carry from your post is that I must be crystal clear in the cert and with the client the extent and limitations of the inspection. And perhaps add the caveat that what is not looked at may not be safe. After all, surveyors are no different. We paid a lot of money to have a structural survey on our house which it turns out was a solid property. Since moving in wet rot, woodworm and leakage and the surveyor has already carefully covered himself in the wording of the report. C'est la vie?
Hear, hear!
completely agree with OP.
Only thing I’d add, is how important it is to make sure the client knows exactly what you’r testing and noting it down in the “limitations” part of the Cert. This covers your arse and lets them know that I won’t be testing 100% of their installation for £200!!!
Reply to EICR's-Unrealistic expectations in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
4K
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Looking for some advice and timescale here. I'm not an electrician just a tennet with a housing association. I've been offered top floor flat in a...
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...