Electrical fault on lighting

Hi, so I came to replace a down light, thought I’d do a Zs to be sure but there seems to be a bigger issue,
I’ve got:
L-N 240v
N-E 120v
L-E 120v

All on a 6a rcbo (which hasn’t tripped)
Readings directly on rcbo are normal

I’ve checked all accessible N terminations, any advice greatly appreciated
 
Hi, so I came to replace a down light, thought I’d do a Zs to be sure but there seems to be a bigger issue,
I’ve got:
L-N 240v
N-E 120v
L-E 120v

All on a 6a rcbo (which hasn’t tripped)
Readings directly on rcbo are normal

I’ve checked all accessible N terminations, any advice greatly appreciated
Hi, Check for water ingress into pendant/junction box. If you have a lot of LEd's on that circuit try changing a LED lamp for a halogen. check for single switch drops as this can cause capacitance.
 
I’ve got:
L-N 240v
N-E 120v
L-E 120v
As per Westward - it's what you get when the CPC is not connected to ground. It's caused by EMI suppression capacitors (CY below), presumably in an LED driver on the circuit, where the capacitors from L to E and N to E form a potential divider giving the 120V on E.
The fault is most likely the lack of continuity in the CPC, nothing else.

IMG_0900.jpeg
 
Thanks for the replies, the circuit concerned supplied a bedroom, the landing and the bathroom, I ran a trailing lead to continuity test the earth from various points; as you’ll see it was not an obvious trace… I found 5 unterminated earths at the DB end hidden in a nest of cables. Apparently this was rewired few months ago…491CFF3D-6382-47BA-BB7E-B3DA63AA7B0F.jpeg
Hi, so I came to replace a down light, thought I’d do a Zs to be sure but there seems to be a bigger issue,
I’ve got:
L-N 240v
N-E 120v
L-E 120v

All on a 6a rcbo (which hasn’t tripped)
Readings directly on rcbo are normal

I’ve checked all accessible N terminations, any advice greatly appreciated
 
Thanks for the replies, the circuit concerned supplied a bedroom, the landing and the bathroom, I ran a trailing lead to continuity test the earth from various points; as you’ll see it was not an obvious trace… I found 5 unterminated earths at the DB end hidden in a nest of cables. Apparently this was rewired few months ago…View attachment 124770
That's what my hair used to look like in the morning when I had some, joking aside that needs a good tidy up before you do anything else and you might find along the way you find the fault. Those Din rail connectors can be a bit tricky if you're not familiar with them. Check that haven't clamped on the insulation of the lighting cable.
 
Thanks for the replies, the circuit concerned supplied a bedroom, the landing and the bathroom, I ran a trailing lead to continuity test the earth from various points; as you’ll see it was not an obvious trace… I found 5 unterminated earths at the DB end hidden in a nest of cables. Apparently this was rewired few months ago…View attachment 124770
Botch it and scarper strikes again.
 
It’s an unusual installation for a house, although I’ve seen things like that in very big houses.
 
It's the TV or amplifier or more seriously your earth isn;t earthed. Double insulated, but chasis floats up to half way.
I found this 15m up on a TV aerial mast (connected to the shield on the cable from a tuner) - and was very unhappy.
 