Electrical problem with Grundfos macerator

That does not look good at all! Far too busy in there, and putting a lot of strain on the FCU.
Can't see any sign of a flexible there? The connection to Nout looks like another solid cored cable.
 
That does not look good at all! Far too busy in there, and putting a lot of strain on the FCU.
Can't see any sign of a flexible there? The connection to Nout looks like another solid cored cable.
what would you suggest i do? There are no flexibles. all ins and out are the same. Grey insulation stiff wires. 4 sets in total. 3 in and one out.
 
Last edited by a moderator:
It appears to be a flexible at the macerator.
yes. There is this at the other side of the toilet. Cant get a better picture that that. the solid core wiring is behind tiling.
 

Attachments

  • 20220305_001252[1].jpg
    20220305_001252[1].jpg
    199.4 KB · Views: 71
  • 20220305_001321[1].jpg
    20220305_001321[1].jpg
    184.3 KB · Views: 74
With the power off and fused connection unit switch off, test continuity from L, N and E at the load side of the FCU to the corresponding terminals in the macerator. It seems likely the neutral is broken at the dodgy taped-over terminal block connection in the last pic. That should not be there, suggests the cable was too short and they didn't have the right materials to extend it. Looks like 'plumber's wiring.'
 
With the power off and fused connection unit switch off, test continuity from L, N and E at the load side of the FCU to the corresponding terminals in the macerator. It seems likely the neutral is broken at the dodgy taped-over terminal block connection in the last pic. That should not be there, suggests the cable was too short and they didn't have the right materials to extend it. Looks like 'plumber's wiring.'
thank you. i will wait til daylight and give that a go
 
I think most on here would agree that you urgently need the services of a competent electrician. That wiring is extremely dangerous, and there are other issues, such as the apparent lack of a local isolator or a remote one that can be locked off.
 
Yes, I will be reaching out to our local electrician. I would like to thank everyone. It looks like there is a break in the neutral line.
Thanks for the help. 🙏
🙏
 