Hi,
I am new to the forum. I am a homeowner and would like to check if an electrical installation carried out last month is within the regs. I have not yet paid the installer who subcontracted the electrical work to an electrician.
Two separate items in the same shower room listed below.
Item 1.
A 2.5mm twin and earth cable has been spurred off a 13 am socket to power an underfloor heating mat in the shower room. Wattage for heating matt 368W. The socket is on the landing outside the shower room. The cable crosses two joists. The electrician cut small holes in the plasterboard, notched the joists and ran the cable through notches to a switch fused spur. Cable is 8mm below the surface. No clips or metal plates were used over the cable where it crossed the joists. Cuts in plasterboard then covered with a piece of tile backing board, filled and sanded.
The fused spur and thermostat are located 138cm from the shower cubicle edge and 39cm from the sink edge.
Item 2.
Two 24v LED strip will be installed within the tiled shower cubicle for illumination. Low voltage cabling run from LED strips to dry lining box in the wall above the shower cubicle door. This houses the driver connected to the lighting circuit. Dry lining box covered with a blanking plate. 2cm from the edge of the shower cubicle to the edge of the dry-lining box and plate.
I would appreciate advice as to whether these installations are appropriate or whether I need to raise concerns with the installer.
I am new to the forum. I am a homeowner and would like to check if an electrical installation carried out last month is within the regs. I have not yet paid the installer who subcontracted the electrical work to an electrician.
Two separate items in the same shower room listed below.
Item 1.
A 2.5mm twin and earth cable has been spurred off a 13 am socket to power an underfloor heating mat in the shower room. Wattage for heating matt 368W. The socket is on the landing outside the shower room. The cable crosses two joists. The electrician cut small holes in the plasterboard, notched the joists and ran the cable through notches to a switch fused spur. Cable is 8mm below the surface. No clips or metal plates were used over the cable where it crossed the joists. Cuts in plasterboard then covered with a piece of tile backing board, filled and sanded.
The fused spur and thermostat are located 138cm from the shower cubicle edge and 39cm from the sink edge.
Item 2.
Two 24v LED strip will be installed within the tiled shower cubicle for illumination. Low voltage cabling run from LED strips to dry lining box in the wall above the shower cubicle door. This houses the driver connected to the lighting circuit. Dry lining box covered with a blanking plate. 2cm from the edge of the shower cubicle to the edge of the dry-lining box and plate.
I would appreciate advice as to whether these installations are appropriate or whether I need to raise concerns with the installer.