Hi,
I am new to the forum. I am a homeowner and would like to check if an electrical installation carried out last month is within the regs. I have not yet paid the installer who subcontracted the electrical work to an electrician.
Two separate items in the same shower room listed below.
Item 1.
A 2.5mm twin and earth cable has been spurred off a 13 am socket to power an underfloor heating mat in the shower room. Wattage for heating matt 368W. The socket is on the landing outside the shower room. The cable crosses two joists. The electrician cut small holes in the plasterboard, notched the joists and ran the cable through notches to a switch fused spur. Cable is 8mm below the surface. No clips or metal plates were used over the cable where it crossed the joists. Cuts in plasterboard then covered with a piece of tile backing board, filled and sanded.
The fused spur and thermostat are located 138cm from the shower cubicle edge and 39cm from the sink edge.
Item 2.
Two 24v LED strip will be installed within the tiled shower cubicle for illumination. Low voltage cabling run from LED strips to dry lining box in the wall above the shower cubicle door. This houses the driver connected to the lighting circuit. Dry lining box covered with a blanking plate. 2cm from the edge of the shower cubicle to the edge of the dry-lining box and plate.
I would appreciate advice as to whether these installations are appropriate or whether I need to raise concerns with the installer.
The cable installation is fine providing is has 30ma RCD protection.
The location of the spur is outside of the zones so that is fine.
It is probably far away enough from the sink so as not to be affected by water splashes (zones do not apply around sinks).
The blank plate looks further than 2cm from the shower cubicle. How high from the floor is it, 2.25m and above is outside of the zones. The SELV source can be in zone 2 provided it has 30ma RCD protection and some would argue being in the wall cavity puts it outside of the zones.
Thanks for your reply and the helpful advice.
The blank plate is 1875mm off the floor, and yes you are right, it is 120mm from the shower cubicle, apologies for the typo.
I would have preferred to see either a metal plate over the cable where it runs close to the surface over the joist or the cable run through the centre of the joist. Both would have then protected it from a nail.
However one could argue that there is a horizontal line from the switched spur to the 13am socket on the other side of the wall. Therefore a quick inspection of either before drilling into the wall would reveal the cable pathway.
The cable is in a permitted zone so it is fine.
Don't forget you need at least Minor Works certification for those works.