Hi Simlec I think what you said is the way to go will do it all in T&E and switch through a fuse spur no need to be complicating things any more got the information I need from you all thank for being there on Sunday night Hope you all have a good week
Regards Plugpass
 
Hope we have helped, if UPS batteries are over 5-10 years old you are onto a expensive looser, so go self contained EM with T&E All the best
 
If the EMG lighting is on the main lighting circuit the emergency lights will come on if there is no power to the other lights, which is what you want. If they're on their own circuit the main lights could go off but the EMG lighting stays in charging mode and with the lights switched off.

Provided the fittings are powered locally (as is usually the case) you should be able to use T&E - if anything happens to the cable the worst that will happen is the light will come on.

very well put spot on
 
Hi Simlec I think what you said is the way to go will do it all in T&E and switch through a fuse spur no need to be complicating things any more got the information I need from you all thank for being there on Sunday night Hope you all have a good week
Regards Plugpass

I really hope you are not...this em system needs to be fed locally off the lighting breaker via a em test switch,to all em lighting feed in this area, as most of us have posted.......I am becoming concerned you should be posting in the the diy forum
 