I've got a job to install a swim jet in an outdoor swimming pool and I want to fit an emergency stop button near the unit. What I'm looking for is some info on whether I can get an emergency stop that I can fit between the rotary isolator and the jet or do I have to wire it through a contactor? The swim jet is rated at 16a. The isolator is fitted in the pump house which is 3m from the swim jet, do you guys think I even need an emergency stop? I personally think it would be best.
 
go by manufacturers instructions. if it says fit a stop, fit one. if not, don't bother.
 
Is this a domestic or commercial installation? If it's domestic then it is a grey area, it's it is commercial then it's a legal requirement.

As for the E-Stop, get one (if you decide too) that is push to break but requires a key to unlatch to re-energise, if you want it simple. failing that you will need to install a contactor and control wiring. If it's commercial, then go with the contactor at source and use a 12/24V control circuit to kill the contactor when depressed, but within the control circuit I would add a no volt relay so that resetting the E-Stop will not automatically start the machine up, you would need to go to the shed and press a rest that re-energises the relay.
 
The pool is in the customers garden, so domestic. The isolator is just inside the pump house door that's not locked( the door that is), so is easily accessible. Personally if any of you guys were doing the job would you fit an emergency stop, say on the pool edge?
 
Definitely SELV in a domestic environment and as Tel said, if the manufacturers recommend it then I would fit it because to not do so could be a greater headache of something goes wrong 6 months after you walk away..
 
Cheers guys, like I said it doesn't specifically ask for an emergency stop but shows an emergency switch that disconnects both poles! Personally I think the isolator will be enough but I'll give the client the option. It's always extra work I suppose!
 
just looked at section 702 swimming pools.......

and no switchgear of any voltage in zones 0 + 1. ( 702.53)

so no emergency stop button at poolside.
case closed.
 
Cheers guys, like I said it doesn't specifically ask for an emergency stop but shows an emergency switch that disconnects both poles! Personally I think the isolator will be enough but I'll give the client the option. It's always extra work I suppose!

A cheaper alternative would be a local commando plug and socket...water proof and good for killing all poles instantly...
 