Come on Mr. Skelton describe for us the different roles of 'equipotential bonding conductors' and 'supplementary equipotential bonding conductors'.
Put your money where your mouth is so to speak.
 
Hi Dave,

ive missed you, just wanted to refer you to a question i posted on the IET site, my daughter has shoes with brass buckles should these ne bonded? what about door handels and hinges?
 
equipotential bonding conductors will keep extraneous conductive parts at same potential, supplementary bonding conductors will keep simultaneously accessible exposed conductive parts and extraneous conductive parts at same potential in event of a fault......extraneous = introduces an earth potential.......exposed = conductive part of equipment which can be touched but not normally live but can become live under fault conditions...
 
equipotential bonding conductors will keep extraneous conductive parts at same potential, supplementary bonding conductors will keep simultaneously accessible exposed conductive parts and extraneous conductive parts at same potential in event of a fault......extraneous = introduces an earth potential.......exposed = conductive part of equipment which can be touched but not normally live but can become live under fault conditions...

Well said that man.

Going off the advice being given should I now run a supplementary bonding conductor between my metal outside light and the big wet tree that's within arms reach of it?
Do I bond to a branch/the trunk or one of the roots? :)
 
if you will insist on extending your hand to feed the troll, what do you expect?

Come on Tel, don't be so insulting to trolls :D

Come on Mr. Skelton describe for us the different roles of 'equipotential bonding conductors' and 'supplementary equipotential bonding conductors'.
Put your money where your mouth is so to speak.

Not that I feel the great need to justify myself to you but hey ho.

Main equipotential bonding conductors connect together the installation earthing system and the metalwork of other services. The purpose is to limit the value of touch voltages by bringing all extraneous conductive parts to the same potential (below 50V) in the event of a fault.

Supplementary bonding conductors connect together exposed conductive parts and extraneous conductive parts that are accessible at the same time ie, metalwork which is not associated with the electrical installation but which may provide earth potential giving rise to shock, extraneous conductive parts that are not reliably connected to the MET or exposed conductive parts that are not reliably earthed. The purpose of supplamentary bonding is also to equalise potential difference in the event of a fault however it is classed as additional protection therefore it is there to save life only.

Finding out whether something is extraneous is as simple as an IR test between 'it' and the MET. In my case I would class anything that falls below 45kohm as an extraneous conductive part (assuming a body resistance of 1kohm) as 5ma to the touch is the maximum value of current that can be percieved as electric shock. Others are happy to use 22kohm.

A simplistic explanation I know, however I don't have much time these days to enter into pointless ego boosting discussions online, as such this will be my last post on this subject. David, please mate, just stop advising others when you don't know what you're talking about.

Best regards.
 
telectrix,
Hello again, are you going to explain how an RCD would have saved the day, or are you just on the wind up again?
think mA and imballance fella..if she got a belt of off this..then she represented a fault path yes..
and so there would have been an imballance as a result on the live conductors yes..
go away cockburn and look at how RCDs work.....
 