Hi all. trying to get to grips with cable calculations and in particular when in trunking. OSG 7.1(i) gives you your tables with reference methods but does not list method B. Table 7.1 (ii) gives you your ratings for installation methods and B is greater than say, reference method 100, so why is it that method B is not in the main table?? Perhaps you could help me with an example? say a 10mm cable in trunking with one ring circuit (both 2.5mm cables). I know I should derate those cables. Where do I start?? Many thanks
 
i've not got the latest green osg, in my red osg, the tables are different , but i think it's because the OSG does not consider T/E in trunking. so if that's the case, derate your cables by the same ratio as given for singles in trunking.
 
It depenss what you are trying to find out. On site guide and regs book both have detailed explanations in to all calculations needed. For example, to find the current carrying capacity of a cable you take the overcurrent device rating (In) and divide it by the appropriate rating factors gien in tables 6A-F this includes ambient temperature grouping and thermal insulation.

I dont have new on site guide. But information is still the same.

A 2.5mm cable cannot take over 24A when enclosed in trunking. 10mm cable can take up to 57A.

You could apply the grouping factors to the cables and this would be a lower amount as the table does not apply the grouping factor and thermal insulation.

Hope his helps some.
 