I will soon be installing an Ohme Home Pro EV charger for a customer and this manufacturer was the customers choice. This will be the first EV charger that I have installed.
However, I was looking at purchasing a Megger EVCA-210 EV charge point adaptor so I can use my Megger MFT 1710 multi function tester to carry out the required testing. It was at this point that I realised that my MFT 1710 is not capable of carrying out the 6mA DC RCD test on the charger.
The Ohme Home Pro has a 'built in' Type A 30mA DC 6mA RCD and PEN fault detection conforming to BS7671 regulation 722.411.4.1 (iv) and the charger is supplied with a 'Statement of Compliance' from the Manufacturer.
The circuit supplying the Ohme charger will be protected by a Type A double pole 30mA RCBO. Apparently it is not a problem to install a Type A RCD / RCBO upstream.
The problem is it looks like I may have to purchase (if I wish to stay with Megger) an MFT-X1 and with the EV charge point adaptor and the best price I can find is about £1750 for both. The MFT-X1 is capable of carrying out the 6mA DC RCD test.
I could buy a Metrel for about £775 + the adaptor. I asked the NICEIC technical help if I can avoid doing this test and put it down as a 'Limitation' and they said No.
I would be interested to hear what other Electricians say.
 
You will have to install an RCD upstream the one incorporated into it will not comply with BS7671.
 
You will have to install an RCD upstream the one incorporated into it will not comply with BS7671.
The statement in the original post about compliance of the 'built-in' protection appears to accurately reflect the manufacturers specification and certification.
Are you saying there are other requirements of BS7671 that the product or installation doesn't comply with?
 
Last edited:
The statement in the OP's original post about compliance of the 'built-in' protection appears to accurately reflect the manufacturers specification and certification.
Are you saying there are other requirements of BS7671 that the product or installation doesn't comply with?
RCDs incorporated into EV chargers are generally pcb based and are not produced to the standards recognised by BS7671. The EV charger requires RCD protection as per BS7671 and as such the internal unit cannot be relied upon to provide that unless you list it's provision as a departure. EV charger manufacturers will tell you an upstream RCD should be fitted which satisfies BS7671.
 
Bs7671 only refers to the fixed wiring of a building, not the product that is connected to it.
This is true but some installers believe the built in RCD satisfies the requirements in BS7671 to provide the EV charger with RCD protection, it does not.
 
I will soon be installing an Ohme Home Pro EV charger for a customer and this manufacturer was the customers choice. This will be the first EV charger that I have installed.
However, I was looking at purchasing a Megger EVCA-210 EV charge point adaptor so I can use my Megger MFT 1710 multi function tester to carry out the required testing. It was at this point that I realised that my MFT 1710 is not capable of carrying out the 6mA DC RCD test on the charger.
The Ohme Home Pro has a 'built in' Type A 30mA DC 6mA RCD and PEN fault detection conforming to BS7671 regulation 722.411.4.1 (iv) and the charger is supplied with a 'Statement of Compliance' from the Manufacturer.
The circuit supplying the Ohme charger will be protected by a Type A double pole 30mA RCBO. Apparently it is not a problem to install a Type A RCD / RCBO upstream.
The problem is it looks like I may have to purchase (if I wish to stay with Megger) an MFT-X1 and with the EV charge point adaptor and the best price I can find is about £1750 for both. The MFT-X1 is capable of carrying out the 6mA DC RCD test.
I could buy a Metrel for about £775 + the adaptor. I asked the NICEIC technical help if I can avoid doing this test and put it down as a 'Limitation' and they said No.
I would be interested to hear what other Electricians say.
The 6mA DC test is not an RCD test, but rather a test of the RDC-DD. There is no requirement in BS 7671 to test this device. As @westward10 has pointed out you will need to install your own RCD upstream which breaks all live conductors. (I note you have stated that you have done this.)
 