Is it acceptable to use a TNC-S (PME) type earthing system on a caravan site for a permanent building?

Is it acceptable to use a TNC-S (PME) type earthing system for earthing a static caravan (the chassis would need to be earthed for this)?
 
do you think by myself putting on first message 'only if you have nothing better to do has put them off;) your a man topquark
 
should i be looking at permanent building , do they see caravan as tow away normally but as you have said permanent
 
who declares the date for the first inspection and test of an installation following initial verification?
 
Have a read of section 708 in the new edition. Generally it is thought that PME is not allowed on a caravan site. There is however an exception that allows it to be used for permanent buildings IE offices etc. But it should NEVER be used for feeding either static homes or mobile caravans.
 
What is the maximum Zs for a circuit protected by a 30A BS3036 Fuse?

1.09 ohms tabe 41.2 and which i would multiply by 0.8 to get my max value in the real world

What if it is measured at 20 degrees C?
 
Last edited:
i can read the question you asked now...
Have a read of section 708 in the new edition. Generally it is thought that PME is not allowed on a caravan site. There is however an exception that allows it to be used for permanent buildings IE offices etc. But it should NEVER be used for feeding either static homes or mobile caravans.
 
With the earthing conductor, Table 54.1 only applies to conductors that are buried.
There is no requirement to provide sheathing or even insulation for an earth conductor.
With the Caravan, it all depends on how you define static.
Residential caravans that are not intended to be moved, are regarded as being permanent buildings.
As such they can be connected to a PME system.
 