you must have some right slappers in surrey then.
I use this book....
Electrical Installation Design Guide: Calculations for Electricians and Designers - IET Electrical
...which has a much better section on demand and diversity than the OSG, and always do a turn-everything-on-clamp-test before any new works to help inform the design.
Des I agree form filling is a pain, so I got a tester that downloads all the results and put them in all the right boxes does it ****** it chucks results all over the place so back to pen, tea, smoke
Pict
Agree Clamp for max demand/load and get the job done as said the only time i think you'd be near the 100A is christmas day !
Local then ! Im in Woodley !
Hi guys,
I have a similar problem and again Im struggling with diversity. These are the circuits I have
1, Electric boiler, 63a but will be put on a 50a mcb
2, Electric boiler 2, 38a but will be on a 32a mcb
3, Kitchen ring, 32a
4, Rad 1, 16a
5, Rad 2, 16a
6, Cooker, 32a
7, Lights 1, 6a
8, Lights 2, 6a
9, Lights 3, 6a
Im not sure why 2 electric boilers are required, and if ive applied diversity correctly I also feel I have a problem, I know there likely hood of everything running at full demand is unlikely and a new 100a fuse is capable of carrying 120a - 130a but just need some advice.
Steven
add all you final circuits up take your highest breaker out then x by 40% then add your highest back in thiss will give you your maximin demand and you will know if you can add any more circuits on board (note result should not be rated higher than your suplyers main fuse)
I worked out the diversity for my house using the OSG and got >130A. It has run for many years on a 60A fuse, which has got a bit hot but has not blown. Cut the load down a bit now so no problem.
At a couple of years later they may have sorted it bud
must have plenty of circuits in house if your m/d calculation came out at 130a ? are you shore you done calc correct !
it dose show you that diversity actually works hence your 60a fuse not blowing........
do you even bother to look at the thread date ?
lol , wot a doughnut ;-)
I think that max. demand and diversity is an ongoing syndrome that many people have problems with and is often useful to resurrect old threads to see as continuity as opposed to kicking off with new ones.
Now back to those slappers .................
The ongoing problem for new electricians and the like with MD/Diversity worries, is the totally misleading values and information contained in BS7671 and it's OSG's. And it's not helped any, by having to use this data in C&G examinations etc!! The only example that actually works, is for cooking loads, and that's been around for over 60+ years!! The rest can literary all be slung in the bin for what use they are to any electrician. You'll not find a single Design Engineer even look at this section of BS7671, let alone apply any of it!! lol!!
sherratts,
Engineer54,