Discuss Fan Isolator in the Australia area at ElectriciansForums.net

E

eskimo39

Hi guys, is a Fan Isolator a must??

I have been asked to change a fan in a friends bathroom and upon inspection have found it to be wired directly to the lighting circuit just above the rose with no isolator available.

It is a standard fitting which only comes on with the lights and goes off immediatley.

Cheers
 
Hi guys, is a Fan Isolator a must??

I have been asked to change a fan in a friends bathroom and upon inspection have found it to be wired directly to the lighting circuit just above the rose with no isolator available.

It is a standard fitting which only comes on with the lights and goes off immediatley.

Cheers
need a selv opperated fan with a triple pole isolator mounted ouside the bathroom check zones and remember this is a special location and comes under the scope of part p. regarding standard fitting their are a few types avalible but id fit the time delay type and these will normally be preset to go off after 5 mins you can adjust these but 5 mins is normal.
regards
Tony.
 
Last edited by a moderator:
Hi guys, is a Fan Isolator a must??

I have been asked to change a fan in a friends bathroom and upon inspection have found it to be wired directly to the lighting circuit just above the rose with no isolator available.

It is a standard fitting which only comes on with the lights and goes off immediatley.

Cheers



yes and no
theres noting stopping you replacing like for like, even though it's in a special location no notification is ness

personally i would fit an isolator somewhere if poss, trouble is as you alter the circuit then it becomes notifiable, and you should be adding rcd protection as well.
check bonding in bathroom, whilst you at it and check what zone fan is in if ceilings are above 2.25m high then its outside of zones and mains fan is ok

can you not get a dp pull switch in a corner somewhere as isolator if not a timer model?
 

Reply to Fan Isolator in the Australia area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
640
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
589
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...
Replies
2
Views
832
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock