hi all
wonder if anyone can clear this up.
installing 2 holiday flats on the side of a pub.building control have told me i need a 60l/s ex fan in the kitchen.
the kitchen in this case is a cooker-sink-fridge and a 300 unit and 600 unit.
its part of the lounge/hall of the flat.
the kitchen extractor is above the cooker-hob on the wall at 1900mm high.

i was under th impression that a 30l/s was the min under these circumstances.

is the final word down to the inspector??

i ask this because 18 months ago a building inspector told me i needed a airflow test for a job we were doing at the time and made a huge fuss.he basically told me that NO AIRFLOW TEST..NO SIGNING OFF THE JOB !..
but after a few weeks and a few phone calls he called the builder(not myself) and said that this was not required.many hours were lost by myself due to this.


all replys greatfully accepted..

vitoboy
 
Extract Rates for Kitchens (minimum)...
30 l/s (litres per second) adjacent to a hob.
60 l/s (liters per second) elsewhere.
 
Going off kilmos reply sounds like he's just quoted you the max value to be on the safe side.
 
(Adjacent to a hob means either –
(a) incorporated within a cooker hood located over the hob; or
(b) located near the ceiling within 300 mm of the centreline of the space for the hob.

I'm busy on a kitchen install at the moment and have had building control questioning it
 
How do they achieve these air flow results? If the fan holds up a piece of big roll it 30l/s, piece of A4 it's 60l/s and a bag of sand it's warp speed :)
 