Faulty meter ?

A

akhinn

Hi,

I recently bought a house with only electricity and no gas. The provider is British Gas.

The thing is that the 6th digit in the meter is going up every second regardless of any appliance on or off.
It went from 153623 to 155054 in about 14 minutes.

( The details on the meter : Telemeter Series K , Tariff Domestic E7 )

Would that be a faulty meter or is this expected with that kind of meters ?

Many thanks in advance
 
All you can do is report it to BG.

is the 6th digit the red one? Would that be measuring 1/10th a unit?

As above, turn off the board, not just individual circuits.
It says E7, so have you got off peak heating? There will be a board for that too. Possibly an immersion water heater you maybe don’t realise is still on.
 
A picture of the meter would be helpful. Also a pic showing the whole area including any boxes with wires going to them
 
If you switch off the whole house at the main isolator and the meter keeps going it is probably a faulty meter.

However, it is far more likely that you have an unknown load draining power. That could be heating / immersion heater / etc that is supposed to take power but should be off (as mentioned above), or it might be a wiring fault dumping power in to the earth but not enough to blow a fuse, etc.

As above, a picture can show folks here a lot more than you might imagine so that is a good starting point. Depending on the type of board some tests / potential faults are easier to safely identify by a home owner, but it may be a case for getting an electrician in to fully check it out.
 
Those readings suggest a usage of 143kWh in 14 minutes!. That's impossible.

Is the meter definitely displaying energy usage rather than something else?

Edit: was the time 15:36 when you took the first reading and 15:50 when you took the second ?
 
Last edited:
Unless you have one of these in the garden
1630575110744.jpeg
I think that the readings are incorrect by a factor of 100, could a decimal point be missing from them?
 
Last edited:
I think that the readings are incorrect by a factor of 100, could a decimal point be missing from them?
Even by 100 that is still about 27A going astray!

A crazy meter is looking like one possibility, or somene has a pot farm secretly fed from it!
 
A picture of the meter would be helpful. Also a pic showing the whole area including any boxes with wires going to them
Sure , just attached.

Many thanks
 

Attachments

  • thumbnail_IMG_0485.jpg
    thumbnail_IMG_0485.jpg
    156.4 KB · Views: 70
You only give the first 5 digits, anything after the decimal point you omit.

However from your OP the readings are way to high (in 14 minutes)
Contact your supplier may need meter exchange
 
Last edited:
y five digits, and you 'ignore' the sixth 1/10 digit.

Those readings suggest a usage of 143kWh in 14 minutes!. That's impossible.

Is the meter definitely displaying energy usage rather than something else?

Edit: was the time 15:36 when you took the first reading and 15:50 when you took the second ?

Ahh , that should be it yes. I wasn`t aware of the display modes. Sorry for taking time , and thanks as I was really puzzled...
 